  • Any central heating guys out there I need a bit of advice.

    Any central heating guys out there I need a bit of advice.
    I have pretty old boiler fitted 1992 yes that old it's done well lasting this long.
    Any way the water pressure is not holding in the system I would top it up once a year but now I'm having to do it every couple of days.
    It's dropping from 1.5bar to near nothing in couple of days I can't find any leaks on the radiators last time I checked the pipes under the floor there was no leaks.

    Could it be the heat exchanger in the boiler or is it something else?
    Hoping I don't have to change it at the moment as money is tight but if I do anyone in North West fancy fitting new one?
    Raptor 30v2
    Skya 500 x 2 one to be Scale Bo 105
    Copter X450 x 2
    Trex 250 x 2
    Mcpx
    Raven wing.
    Suhkoi
    Anx Floater
    Radjet 800


    DX7
    Phoenix v4

    Proud to be member of SCHA

    Log Cabin for Hire in Snowdon.


    http://www.youtube.com/user/streetlu...s?feature=mhee

  • #2
    check your pressure relief pipe outside.
    probably a flat expansion vessel on the boiler. what model is it
    1x EGS, TREX 450 PRO DFC & 130X. DX9 radio. No idea what i am doing trying to fly

    Comment


    • #3
      Hi, I am a gas engineer. Sounds like your pressure relief valve is letting by. There should be a pipe outside, behind the boiler, is that dripping?

      With your system water cold, set the pressure to 1bar. Now put the heating on, and watch the needle. Does it climb fairly quickly to 3bar, then the pressure drops? If so, your expansion vessel is knackered. Easy to repair, you can cut into any flow and return pipe and fit an external pressure vessel. The Pressure relief valve will need to be replaced, but they are cheap, around £15-20

      Let me know, and I will keep an eye on this thread for you.
      Henseleit TDR V-Bar x2
      SAB Goblin 700 V-Bar
      SAB Black Nitro V-Bar YS91 Tareq SRX
      T-Rex 700e DFC V-Bar
      T-Rex 700N MAJ DFC V-Bar YS91 Tareq SRX
      Synergy N7 V-Bar OS105 HZ-R
      Synergy E7se V-Bar
      Synergy N5c FBL V-Bar
      Gaui NX7 V-Bar YS91 Tareq SRX
      T-Rex 550 E FBL V-Bar
      Gaui NX4 V-Bar
      V-Control

      Proud owner of TWO!! Platinum Stars!

      Comment


      • #4
        yes, sounds like the expansion vessel has lost the pressure. you can re pressurise it using a foot pump but it's probably goosed. I by passed my vessel and added a larger external one.

        Dan :peaceful:

        TREX 550X - Beastx HD Pro
        GOBLIN 570 - V-Bar Neo Pro

        Taranis X9D Plus

        neXt Sim

        AccruRc Sim

        Proud wearer of 3 X EGS

        Comment


        • #5
          Let me know what boiler it is. If you can identify the expansion vessel (usually behind the boiler accessible from the top by the flue) there will be a screw on cap just like a car tyre valve. Remove the cap, and press the valve in (like you would to remove pressure from a tyre) If you get water coming out rather than compressed air, for sure you need a new expansion vessel. You can get on from Screwfix like this [url=http://www.screwfix.com/p/expansion-vessel-12ltr/46517]Expansion Vessel 12Ltr | Screwfix.com[/url] and a fixing kit like this [url=http://www.screwfix.com/p/expansion-vessel-mounting-bracket/86194]Expansion Vessel Mounting Bracket | Screwfix.com[/url]# then just fit a 'T' into a heating pipe anywhere in the system, and connect this vessel with a flexi tap connector like this [url=http://www.screwfix.com/p/flexible-tap-connector-22mm-x-x-300mm/15015]Flexible Tap Connector 22mm x ¾" x 300mm | Screwfix.com[/url]

          If only air comes out of the valve, it can be re pressurised with a car foot pump. To do this, you have to first relieve all pressure from the heating water, them pump the vessel up with 1bar of air. The needle on the boiler pressure gauge should not raise at all, if it does, again relieve the water pressure. Now check air is 1bar, and refill heating to 1bar. Dont forget to replace the PRV though, because once disturbed at that age, it will never reseat, and will continue to drip.
          Henseleit TDR V-Bar x2
          SAB Goblin 700 V-Bar
          SAB Black Nitro V-Bar YS91 Tareq SRX
          T-Rex 700e DFC V-Bar
          T-Rex 700N MAJ DFC V-Bar YS91 Tareq SRX
          Synergy N7 V-Bar OS105 HZ-R
          Synergy E7se V-Bar
          Synergy N5c FBL V-Bar
          Gaui NX7 V-Bar YS91 Tareq SRX
          T-Rex 550 E FBL V-Bar
          Gaui NX4 V-Bar
          V-Control

          Proud owner of TWO!! Platinum Stars!

          Comment


          • #6
            The boiler is Myson Midas B I have found all the info on the model and lucky for me it shows all the bits.

            [url=http://85.189.44.185/Baxi/System/DATA/Dx/DS1/installation/2514/I19-2514/I19-2514.htm]Midas - B - Installation and Servicing Instructions[/url]

            Hi, I am a gas engineer. Sounds like your pressure relief valve is letting by. There should be a pipe outside, behind the boiler, is that dripping?

            With your system water cold, set the pressure to 1bar. Now put the heating on, and watch the needle. Does it climb fairly quickly to 3bar, then the pressure drops? If so, your expansion vessel is knackered. Easy to repair, you can cut into any flow and return pipe and fit an external pressure vessel. The Pressure relief valve will need to be replaced, but they are cheap, around £15-20

            I have checked the above and the over flow is not leaking and the water pressure always stays the same I have never noticed it rise?

            Thanks for you help .
            Raptor 30v2
            Skya 500 x 2 one to be Scale Bo 105
            Copter X450 x 2
            Trex 250 x 2
            Mcpx
            Raven wing.
            Suhkoi
            Anx Floater
            Radjet 800


            DX7
            Phoenix v4

            Proud to be member of SCHA

            Log Cabin for Hire in Snowdon.


            http://www.youtube.com/user/streetlu...s?feature=mhee

            Comment


            • #7
              Your Exp Vessel is no 75 in the diagram at the rear of the linked instructions, and your PRV is no 78. Look around the edge of the square tank for the valve, and follow the advise I listed above.
              Last edited by Rctintin; 30-10-2012, 07:17 PM.
              Henseleit TDR V-Bar x2
              SAB Goblin 700 V-Bar
              SAB Black Nitro V-Bar YS91 Tareq SRX
              T-Rex 700e DFC V-Bar
              T-Rex 700N MAJ DFC V-Bar YS91 Tareq SRX
              Synergy N7 V-Bar OS105 HZ-R
              Synergy E7se V-Bar
              Synergy N5c FBL V-Bar
              Gaui NX7 V-Bar YS91 Tareq SRX
              T-Rex 550 E FBL V-Bar
              Gaui NX4 V-Bar
              V-Control

              Proud owner of TWO!! Platinum Stars!

              Comment


              • #8
                the vessell will probably not be knackered.
                You can quite easily pump it back up with a foot pump.

                This is a common issue and easily fixed in most cases with little expense
                1x EGS, TREX 450 PRO DFC & 130X. DX9 radio. No idea what i am doing trying to fly

                Comment


                • #9
                  That amount of water has to be going somewhere.
                  are you confident you checked the correct pipe outside?
                  1x EGS, TREX 450 PRO DFC & 130X. DX9 radio. No idea what i am doing trying to fly

                  Comment


                  • #10
                    True, but at 20 yrs old, I bet it has perished inside. As I said above, check if water is coming from the valve, if it is, new vessel required.
                    Henseleit TDR V-Bar x2
                    SAB Goblin 700 V-Bar
                    SAB Black Nitro V-Bar YS91 Tareq SRX
                    T-Rex 700e DFC V-Bar
                    T-Rex 700N MAJ DFC V-Bar YS91 Tareq SRX
                    Synergy N7 V-Bar OS105 HZ-R
                    Synergy E7se V-Bar
                    Synergy N5c FBL V-Bar
                    Gaui NX7 V-Bar YS91 Tareq SRX
                    T-Rex 550 E FBL V-Bar
                    Gaui NX4 V-Bar
                    V-Control

                    Proud owner of TWO!! Platinum Stars!

                    Comment


                    • #11
                      I've had a quick look at it the expansion tank at the back is hidden at the back I can not see a valve on the tank.
                      There is a valve on this below

                      [ATTACH=CONFIG]50435[/ATTACH]

                      I did find slight leak on 102 automatic air vent.

                      [ATTACH=CONFIG]50436[/ATTACH]

                      General pic of inside.

                      [ATTACH=CONFIG]50437[/ATTACH]

                      I think if it is the expansion tank I'm in trouble.

                      Your fantastic bunch of gents thanks again for help.
                      Attached Files
                      Raptor 30v2
                      Skya 500 x 2 one to be Scale Bo 105
                      Copter X450 x 2
                      Trex 250 x 2
                      Mcpx
                      Raven wing.
                      Suhkoi
                      Anx Floater
                      Radjet 800


                      DX7
                      Phoenix v4

                      Proud to be member of SCHA

                      Log Cabin for Hire in Snowdon.


                      http://www.youtube.com/user/streetlu...s?feature=mhee

                      Comment


                      • #12
                        It is normal for the auto air vents to spit out a bit of water but as long as its not coming out steady then leave it alone.
                        there must be a schraeder valve somewhere that is accesible on the big red exp vessel on the back. obviously do not take any combustion doors off or go anywhere you aint supposed to go ;)
                        if you do find the cap then f you attach a foot pump to it you can check if its flat or not.
                        If it was then you would need to open the ch system by either draining it off from a radiator or you can use the prv(the red valve in the middle of pic 3) You turn it and it discharges the water through the prv pipe. the trick is to turn the valve until it stays open. then you start pumping and you may think its just going out the wall but keep at it as it can take a while to get the pressure into the vessel. if it does pressurise then pump it to 1 bar(average) then remove the foot pump. you would then start to refill the water in the central heating. whilst doing this twist the prv valve a couple of times till it clunks back into place as it normally passes once its been opened.
                        i really cant see that the water is going anywhere else unless you have a leaking rad or pipe. It is normally very obvious if the vessel is flat by touching the end of the 15mm copper pipe going through the wall to the outside.
                        when the vessel is flat and you top up the sys press to 1 bar it heats up expands and discharges through the prv. this cycle continues until the pressure drops.
                        Please take extreme care not to do any work on your boiler that you are not qualified to do mate.
                        If you are really stuck then you can get on contract and have a first fix first visit with british gas for £99 then a monthly homecare contract of your choice.
                        Personally if it was me i would be swapping that boiler for a worcester greenstar combi.